can you spray fire proofing material into sprinkler piping? Yes or No? code reference if any?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
why would anyone want to spray fire proofing into a pipe system designed to carry water? I would say that you can not spray FP into the piping it would be an obstruction.itsasurewin said:can you spray fire proofing material into sprinkler piping? Yes or No? code reference if any?
Maybe pipe was put up, prior to Fire proofing what should of been done!!!!!TheCommish said:why would anyone want to spray fire proofing into a pipe system designed to carry water? I would say that you can not spray FP into the piping it would be an obstruction.
I can't find anything about sainting the pipe. It says the sprinkler heads can only be painted by the manufacturer and pipe must have a protective coating applied where in a corrosive environment and special types of pipe are not used. Since it's not expressly forbidden does that mean it's permitted or is it not permitted because it's not expressly stated? Either way I'm done playing devil's advocate. As I said before my concern would be the added load to the hangers as long as we're talking about steel pipe.cda said:But goes on somewhere to say you canPlus steel pipe is not listed like cvpc is
See above sections talking about painting the pipe
The pipe was installed before the spray proofing was applied and notice that they covered the sprinkler pipes.TheCommish said:why would anyone want to spray fire proofing into a pipe system designed to carry water? I would say that you can not spray FP into the piping it would be an obstruction.
Yeah I saw this requirement and qouted it. Also, noted the added weight and to check every single sprinkler head for overspray residue.tmurray said:NFPA 13 (2007 edition) 6.3.8.2 "All pipe, including specially listed pipe allowed by 6.3.6, shall be marked along its length by the manufacturer in such a way as to properly identify the type of pipe. the markings shall be visible on every piece of pipe over 2ft (610mm) long."...kinda hard to comply with that requirement with fire proofing sprayed onto it...
onto the piping.globe trekker said:Are we talking about fireproofing "onto" sprinkler piping, or "inside" of it?.
Above ground steel pipe is not listeditsasurewin said:Yeah I saw this requirement and qouted it. Also, noted the added weight and to check every single sprinkler head for overspray residue.