Mixed use, services and some retail.What is your business and what was the adjacent space used for?
Mixed use, services and some retail.What is your business and what was the adjacent space used for?
7200You mention being in a 3500 sq ft space and expanding into a 2000 sq ft space. Is 5500 the total sq ft of the building? If not then what is the total sq ft of the building you are in?
It will be art sales and artists work space. It was electronics sales, repair & service.What is and what was the retail?
Probably. The allowable area for the building isn't exceeded, and the fire area is small enough. Other details can have an effect like construction type, other occupancies and number of stories. Assuming type VB, single story M classifications, at 7200ft² you are probably OK. Your DP is the best source of answers. Art sales (Art Gallery????) and artist work space is a little open to interpretation, but if remaining a mercantile it sounds acceptable.
Yes I do have an architect. They say no sprinkler needed. A second architect confirmed. Fire department is firm on needing one.Depends on what part of the IEBC you are using and the type of construction and what year code.. For example a B occupancy with type VB construction can only be 9,000 sq. ft. per 2015 IBC.
Don't you have a architect?
Yes I do have an architect. They say no sprinkler needed. A second architect confirmed. Fire department is firm on needing one.
NFPA Codes, NFPA 13
Wisconsin DSPS Codes: 2013 Wisconsin Act 270.
(g) Additions. Remodeled Buildings and Change of Use. All existing public buildings or places of employment, and all additions shalI conform to this section, as follows: 1. More than 50% remodeled or added. If more than 50% of the gross area of a building is remodeled and/or added, the entire building shall comply with the requirements of this section. 3. The percentage of a building remodeled or added from the date of passage of this Code shall be added together for each remodeling or addition to get the total percentages remodeled or added. 4. Any building with an existing sprinkler system, when making an addition, regardless of size or occupancy, will sprinkler the addition in accordance with National Fire Protection Association 13. 5. If the use of an existing building is changed to a new use, it shall comply with all aspects of this Code.
Municipal Code 5.10.
Additions, Remodeled Buildings and Change of Use. All existing public buildings or places of employment, and all additions shall conform to this section, as follows:
- More than 50% remodeled or added. If more than 50% of the gross area of a building is remodeled and/or added, the entire building shall comply with the requirements of this section.
- If additions to a principal building combine to meet or exceed the limits set forth in Section 5.10(16)(b), the building shall comply with all aspects of this Code.
- The percentage of a building remodeled or added from the date of passage of this Code shall be added together for each remodeling or addition to get the total percentages remodeled or added.
- Any building with an existing sprinkler system, when making an addition, regardless of size or occupancy, will sprinkler the addition in accordance with National Fire Protection Association 13.
- If the use of an existing building is changed to a new use, it shall comply with all aspects of this Code
Currently a B occupancy in the 3500 sq ft space, wanting to use the adjacent 2000 sq ft space with pass through doors. Previous tenant was retail/service and could be considered M and be a possible change of use for that space. Before that it was a bank, definitely a B.If you are strictly an M occupancy then #4 should be the only reason a sprinkler maybe required based on the size of your building
[F] 903.2.7 Group M.
An automatic sprinkler system shall be provided throughout buildings containing a Group M occupancy where one of the following conditions exists:
1. A Group M fire area exceeds 12,000 square feet (1115 m2).
2. A Group M fire area is located more than three stories above grade plane.
3. The combined area of all Group M fire areas on all floors, including any mezzanines, exceeds 24,000 square feet (2230 m2).
4. A Group M occupancy used for the display and sale of upholstered furniture or mattresses exceeds 5,000 square feet (464 m2).