I am working on apartment building 4 stories with area 3950 ft² for each story, building height is 48 ft, and there are two apartments on each floor, the occupant load in each floor is 20, the construction type is IIA.
As per 903.2.8 Group R. An automatic- sprinkler system installed in accordance with Section 903.3 shall be provided throughout all buildings with a Group R fire area.
And as per 903.2.11.3 Buildings 55 feet or more in height. An automatic sprinkler system shall be installed throughout buildings with a floor level having an occupant load of 30 or more that is located 55 feet (16 764 mm) or more above the lowest level of fire department vehicle access.
903.3.1.2 NFPA 13R sprinkler systems. Automatic sprinkler systems in Group R occupancies up to and including four stories in height shall be permitted to be installed throughout in accordance with NFPA
13R.
Can I cancel the sprinkler system from this building based on the height & occupant load conditions?
As per 903.2.8 Group R. An automatic- sprinkler system installed in accordance with Section 903.3 shall be provided throughout all buildings with a Group R fire area.
And as per 903.2.11.3 Buildings 55 feet or more in height. An automatic sprinkler system shall be installed throughout buildings with a floor level having an occupant load of 30 or more that is located 55 feet (16 764 mm) or more above the lowest level of fire department vehicle access.
903.3.1.2 NFPA 13R sprinkler systems. Automatic sprinkler systems in Group R occupancies up to and including four stories in height shall be permitted to be installed throughout in accordance with NFPA
13R.
Can I cancel the sprinkler system from this building based on the height & occupant load conditions?