What do you mean "If"?If you have a back flow preventor as part of the sprinkler riser stack
To me if you put the gauge for the city water main pressure on top of the backflow in the picture,FM William Burns said:The one on the supply side of the alarm/check valve will show you the water system's static pressure +/- 10 psi for the backflow assembly. In this case it looks like an AMES Colt Series. So you would have about 9 psi loss according to Page 2:http://media.wattswater.com/ES-A-C300-C300N.pdf
The backflow meets the second part of your answerFM William Burns said:I'm a bit confused. There should be an alarm check valve to make notification of water flow. NFPA 13 requires a pressure gauge above and below the alarm/check valve [7.1.1.2]. With regards to a "shotgun" riser, there should be alarm/check valves on each riser extending vertical from the horizontal supply.
That is one reason for the system side gaugeBuilder Bob said:true, but the back flow prevent or will indicate water pressure that is supplied from the city and the newer NFPA 13 requires pressure relievers to reduce the surge pressure.... If you do a short drain test with the gauge prior the preventors, are you getting a true water pressure reading when operating the main drains? I think not, the pressure would be higher since the pressure drops in preventors..... thus to get an accurate main drain test it would have to be after the preventors...
Back flow in the buildingBuilder Bob said:Sounds like only one pressure gauge is required...... if the back-flow preventor is outside the building, then the fire sprinkler system doesn't start until is 12" AFF..... (SHOTGUN RISER ONLY ---- Black Pipe - riser with flow switch...)