• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

sprinkler water supply

BSSTG

Gold Member
Joined
Nov 30, 2009
Messages
729
Location
Seadrift, Tx.
Greetings all,

I have an inspection for this pm of the underground water supply piping to a new building for the sprinkler systems. My question is, does this u/g portion of the piping get tested the same as the spinkler piping within the building at 200 psi for 2 hours? This section of piping is fire water supply and will be in between the water meter and the backflow preventer installed within the bldg. NFPA 13 system.

thanksabunch

BS
 
Yes and a minute amount of leakage is allowed

Check the thirst blocks and I witness the flush also
 