Greetings all,

I have an inspection for this pm of the underground water supply piping to a new building for the sprinkler systems. My question is, does this u/g portion of the piping get tested the same as the spinkler piping within the building at 200 psi for 2 hours? This section of piping is fire water supply and will be in between the water meter and the backflow preventer installed within the bldg. NFPA 13 system.

thanksabunch

BS
 
Yes and a minute amount of leakage is allowed

Check the thirst blocks and I witness the flush also
 