Sprinklers above panel

Mr. Inspector

SAWHORSE
Joined
Nov 28, 2009
Messages
4,690
Location
Poconos/eastern PA
2008 NEC 110.26 (f) (1) © Sprinkler protection shall be permitted for the dedicated space where piping complies with this section.

Where in this section tells you the piping complies?
 
I believe they are saying the coverage (spray) can be there, but not the piping.....As far as the "protected from damage" aspect....if something gets hot enough to set the head off, the panel is going to be damaged....
 
The pipe would have to be over 6 feet above the panel with leak protection at least 6 feet above the panel.
 