• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Sprinklers above panel

Mr. Inspector

SAWHORSE
Joined
Nov 28, 2009
Messages
4,139
Location
Poconos/eastern PA
2008 NEC 110.26 (f) (1) © Sprinkler protection shall be permitted for the dedicated space where piping complies with this section.

Where in this section tells you the piping complies?
 
I believe they are saying the coverage (spray) can be there, but not the piping.....As far as the "protected from damage" aspect....if something gets hot enough to set the head off, the panel is going to be damaged....
 
The pipe would have to be over 6 feet above the panel with leak protection at least 6 feet above the panel.
 
many designers here put the sprinkler pipe into the electrical room over the door to avoid conflicts.
 