Looking forward to your public input….Not promoting one interpretation over another, just promoting better code writing.
I agree 100%. One of my favorites in 410 is about doors in stages "likely" to be opened. WTF? And I reviewed the 410 commentary for staff and it was awful. I hope they take some of my suggestions. And a lot in 410 seems to repeat and sometimes contradict other sections.I would prefer less vagueness in favor of more definitive language.
"Associated" can and does mean different things to different people. That is demonstrated in this thread. If it is meant to apply to events only during school hours, then say it. If only for students or faculty, say it. If the "public" is to be included or excluded, start by defining that term, then say it. I don't think it is that difficult to provide metric by which a little more certainty can be arrived at. Is it enough for an architect to put a note on the plans that "only events associated with the E occupancy will occur"? Do we accept what we don't believe, or call someone dishonest?Looking forward to your public input….
Question about how to read this definition's sentence structure: does the phrase "overhead hanging" apply only to the word "curtains"?"BG]STAGE. A space within a building utilized for entertainment or presentations, which includes overhead hanging curtains, drops, scenery or stage effects other than lighting and sound."
If we don't do it, it will be wrong......Either by the industry folks or by the dumb people that have time (not saying they all are as I try my best to participate)...For instance:I have written several code change proposals, and scrapped them all once I realized that as a fully employed code official I just don't have the time and energy to do the work. (Some I scrapped once I realized I also may not have the intellectual chops to do it).
The code writers are us, whomever wants to be. I'm involved out of my passion for the performing arts. I get some help with travel expenses but some expense and all my time is out of my topic. Yes, it does take time. From 1987 to 2005 I figured about 10% of my time. Less since until I (mostly) retired in 2019, now much more.Not trying to throw shade on the code writers,
I think a fundamental problem is the definition of platform leads people to the idea that it's either a stage or a platform, and I don't believe the code requirements support that.Question about how to read this definition's sentence structure: does the phrase "overhead hanging" apply only to the word "curtains"?
Or does it apply to all the other items: overhead hanging drops, overhead hanging scenery, overhead hanging stage effects?
In other words, if I have scenery that is not overhead hanging, can I call it a platform?
Check out:I admit I don't know but wish someone could explain the difference between not a separate occupancy and mixed occupancies.
A "full working stage" - the term SBC used which is by far the most accurate - does work like a chimney or flue. Very well studied after Ringtheatre fire in 1881. Those engineers and the engineer who studied the Iroquois fire and some recent modeling done for NFPA all point to the value of ventilation at the top of the stage to keep audience egress smoke free.I thought I had read a commentary years ago (sorry I can’t get more specific) that the idea of hanging components was related to vertical flame spread, and that a “legitimate stage” had an overhead fly area that might function like a chimney.
In that sense, a platform without those components may be safer.
(Sorry, I’m breaking my own guideline about backing up positions with code references.)
I think a fundamental problem is the definition of platform leads people to the idea that it's either a stage or a platform, and I don't believe the code requirements support that.
Further, whether combustibles are hung or free standing seems irrelevant to the fire hazard. It should be about the amount of combustibles, not how they are supported, which the stage area and stage height tries to measure. Heights and area seem like a tested and proven means to measure some of the hazard.
And in any space used for "entertainment and presentation", whether or not the floor area is raised is not especially relevant to the fire hazard. (Fall hazard different, and probably many hundreds more stage/platform fall injuries and deaths than stage/platform to fire injuries and deaths over last 100+ years.)
Which have never worked.It's also about whether or not there is a proscenium, with a proscenium opening that can be effectively closed with a fire curtain.
Which have never worked.
If the Assembly type spaces are only used by students and staff they can be considered part of the E occupancy. But the reality is that these large assembly spaces in schools commonly get used by the community after hours and on the weekend which then makes the A occupancies.I'm not understanding the direction of "if a school has a gym or auditorium it's an "A". Code specifically says it's an "E" and no separation or reduction of allowable area based upon the "A" use. Yes you sprinkler it (you have to anyway based on "E") and egress it and provide required restroom based upon A use but it's not a separated /non-separated mixed use sort of thing.
Platform vs Stage really is all about hanging/movable drops and lighting or not. A stationary fixed curtain "upstage" suddenly doesn't make it the Met
In reference to platform versus stage it's always interesting when so many people are very sure if the meaning and intent but they disagree.I'm not understanding the direction of "if a school has a gym or auditorium it's an "A". Code specifically says it's an "E" and no separation or reduction of allowable area based upon the "A" use. Yes you sprinkler it (you have to anyway based on "E") and egress it and provide required restroom based upon A use but it's not a separated /non-separated mixed use sort of thing.
Platform vs Stage really is all about hanging/movable drops and lighting or not. A stationary fixed curtain "upstage" suddenly doesn't make it the Met
I don't know what a "non-functioning curtain/fire event" is. I have been looking for an example of when a fire safety curtain actually functioned in an occupied theatre. National and international conferences, many tech theatre bulletin boards and face book groups, the manufacturers and contractors who provide these. Zero. And my estimate of similarly asking if they actually would work, including my own inspection, maybe 50% would close.Are there any recent non-functioning curtain/fire events? I work PT in a full function theatre built in the 30's and the problems I see regarding fire curtain function are either lack of maintenance or by improper installation of cables from speaker or lighting crossing the proscenium line.