One of my coworkers has a situation with a 17-story residential building currently in the design phase. None of the doors from the stair to the residential floors are lockable, but the top floor is a mechanical penthouse that should be locked from the stair side. The mechanical penthouse doors could have fail safe locks with the capability of remote release, but the question is whether locking the mechanical penthouse would result in the need for a stairway communication system. I'm not sure that letting people into the mechanical penthouse during a fire is a great option, but there is another exit on that level so if someone could find their way though the mechanical equipment they could use the other stair. It seems excessive to have the communication system for just that one door, but what do you think?
Here's the language from the 2009 IBC and the Commentary:
403.5.3 Stairway door operation. Stairway doors other than the exit discharge doors shall be permitted to be locked from the stairway side. Stairway doors that are locked from the stairway side shall be capable of being unlocked simultaneously without unlatching upon a signal from the fire command center.
Commentary: Section 1008.1.9.10 requires that all egress doors for interior stairways be readily openable from both sides. It is often desirable to control movement of people within a building and to provide additional security from external threats. This section permits locking of stairway doors from the stair side when all doors are capable of being simultaneously unlocked. Since high-rise buildings are difficult to evacuate and people are often relocated to another floor level during an emergency, access from the stairway to a floor could be essential in a fire or other emergency. Therefore, all stairway doors that are to be locked from the stairway side must have the capability of being unlocked on a signal from the fire command center. The unlocking of the door must not negate the latching feature, which is essential to the operation of the door as a fire door. Section 403.4.7.2, Item 1, by its reference to Section 403.4.5, requires the locking feature to be connected to the standby power system. When the door is unlocked during an emergency, it should not automatically relock on closure. Electrically powered locks should be designed such that when power to the locking device is interrupted, the lock is released. This is intended to enable doors to be operable from the inside of the stairway, and not locked, if power to the lock is interrupted. The building official should review the emergency release operation of stairway doors to determine that they remain unlocked.
403.5.3.1 Stairway communication system. A telephone or other two-way communications system connected to an approved constantly attended station shall be provided at not less than every fifth floor in each stairway where the doors to the stairway are locked.
Commentary: If the stairway doors are locked to restrict reentry as permitted in Section 403.5.3, a two-way communication system must be provided at no less than every fifth floor and must be connected to the standby power system. This system is required to be connected to a constantly attended location, which could be within the building, or to a central station that monitors fire alarms and is manned 24 hours a day, 7 days a week. Use of the fire command center is not recommended, since it may not be constantly attended. The system will permit occupants in the stairway to notify the attended location that the stairway doors need to be unlocked to access another floor or because conditions in the stairway prevent its continued use.
Here's the language from the 2009 IBC and the Commentary:
403.5.3 Stairway door operation. Stairway doors other than the exit discharge doors shall be permitted to be locked from the stairway side. Stairway doors that are locked from the stairway side shall be capable of being unlocked simultaneously without unlatching upon a signal from the fire command center.
Commentary: Section 1008.1.9.10 requires that all egress doors for interior stairways be readily openable from both sides. It is often desirable to control movement of people within a building and to provide additional security from external threats. This section permits locking of stairway doors from the stair side when all doors are capable of being simultaneously unlocked. Since high-rise buildings are difficult to evacuate and people are often relocated to another floor level during an emergency, access from the stairway to a floor could be essential in a fire or other emergency. Therefore, all stairway doors that are to be locked from the stairway side must have the capability of being unlocked on a signal from the fire command center. The unlocking of the door must not negate the latching feature, which is essential to the operation of the door as a fire door. Section 403.4.7.2, Item 1, by its reference to Section 403.4.5, requires the locking feature to be connected to the standby power system. When the door is unlocked during an emergency, it should not automatically relock on closure. Electrically powered locks should be designed such that when power to the locking device is interrupted, the lock is released. This is intended to enable doors to be operable from the inside of the stairway, and not locked, if power to the lock is interrupted. The building official should review the emergency release operation of stairway doors to determine that they remain unlocked.
403.5.3.1 Stairway communication system. A telephone or other two-way communications system connected to an approved constantly attended station shall be provided at not less than every fifth floor in each stairway where the doors to the stairway are locked.
Commentary: If the stairway doors are locked to restrict reentry as permitted in Section 403.5.3, a two-way communication system must be provided at no less than every fifth floor and must be connected to the standby power system. This system is required to be connected to a constantly attended location, which could be within the building, or to a central station that monitors fire alarms and is manned 24 hours a day, 7 days a week. Use of the fire command center is not recommended, since it may not be constantly attended. The system will permit occupants in the stairway to notify the attended location that the stairway doors need to be unlocked to access another floor or because conditions in the stairway prevent its continued use.