Am I dreaming again, or were "fire standpipes" allowed to occupy some of the width in a stairway?
 
2012

[F] 905.4 Location of Class I standpipe hose connections.

Class I standpipe hose connections shall be provided in all of the following locations:

1. In every required stairway, a hose connection shall be provided for each floor level above or below grade. Hose connections shall be located at an intermediate floor level landing between floors, unless otherwise approved by the fire code official.

[F] 905.4.1 Protection.

Risers and laterals of Class I standpipe systems not located within an enclosed stairway or pressurized enclosure shall be protected by a degree of fire resistance equal to that required for vertical enclosures in the building in which they are located.

Exception: In buildings equipped throughout with an approved automatic sprinkler system, laterals that are not located within an enclosed stairway or pressurized enclosure are not required to be enclosed within fire-resistance-rated construction.

2003

[F] 905.4 Location of Class I standpipe hose connections.

Class I standpipe hose connections shall be provided in all of the following locations:

1. In every required stairway, a hose connection shall be provided for each floor level above or below grade. Hose connections shall be located at an intermediate floor level landing between floors, unless otherwise approved by the building official.
 
2012

[F] 403.3.1.1 Riser location.

Sprinkler risers shall be placed in interior exit stairways and ramps that are remotely located in accordance with Section 1015.2.
 
Aside from poor design; are there violations? The handle projects about 2-inches over the red line.

Background information; this is not an accessible route. The outer red line is the edge of the radius (ignore the inside line), it appears oval from the viewpoint.

 