I have a (hopefully) quick question to see how you guys would interpret this particular situation. I have a an I2 facility with two stairwells that have required signage at each level. The stairs run from the 3rd floor to the basement, but there is a partition blocking access from the 1st floor (exit discharge) to the basement. This is a full frosted plexiglass partition, not just a swing gate to keep people from going down the stairs past the exit discharge. There are two doors right next to each other, one is the exit discharge from the 1st floor and the other is exit discharge from the basement. There is no re-entry hardware on the exit doors.
My question is with the stairwell signs. They state the floor level, no roof access, the exit discharge location, and the floors served by the stairs. The problem is that the floors served is listed as 3rd to basement. Would you require these signs to be changed or is this acceptable? I am using IBC 2012 and 1022.9 to try and understand the requirements.
The facility also has a Knox Box giving firefighters all access and they have been given pre-plans showing the stair layouts.
Thanks for any opinions!
My question is with the stairwell signs. They state the floor level, no roof access, the exit discharge location, and the floors served by the stairs. The problem is that the floors served is listed as 3rd to basement. Would you require these signs to be changed or is this acceptable? I am using IBC 2012 and 1022.9 to try and understand the requirements.
The facility also has a Knox Box giving firefighters all access and they have been given pre-plans showing the stair layouts.