I think the original question is asking if the standpipe needs an outlet on the ground floor of the building. The FDC location is a separate issue and isn't necessarily related to the location of the stairway or standpipe.
In the case of the need for a standpipe outlet in the stair on the ground floor of the building, I'd say the answer is yes. Typical fire attack from a standpipe has the connection to the standpipe being made one floor below the fire floor - so in the case of a fire on the second floor the actual connection to the standpipe would occur on the ground floor.