Standpipes are required where?

Joined
Oct 19, 2009
Messages
529
Location
Lincoln
Good morning.

The details on sprinkler systems and standpipes are all very new to me. Especially when trying to figure out the required fire flow (gpm).

I am conducting a code review for a 7,400 S.F. restaurant with an occupant load of approximately 240.

This restaurant will be fully sprinkled.

NFPA 1 Section 13.2.2.4 requires standpipes for "new assembly occupancies, regular stages over 1,000 S.F. in area..."

Question:

Please confirm that a one story restaurant without a stage does NOT require a standpipe system.

Thank you!
 
See IBC 905.3 for when standpipes are required. If you have a stage over 1,000 SF, then the required hose connection can be made from the sprinkler system(905.3.4). I doubt your stage, if any is that large. No standpipe required for your one-story assembly use.
 