2018 IBC, Type V-A construction, R-2.
I have some corner balconies that we are using a steel column to support the corner.
At first I thought I may have to apply fire-proofing to the column per table 601, but IBC 705.2.3.1 exception 3 states balconies of Type V construction "shall be permitted to be of Type V construction and shall not be required to have a fire-resistance rating where sprinkler protection is extended to these areas". We will have spinkler protection at balconies.
Is it correct to interrupt that that exception extends to the steel column as well?
I have some corner balconies that we are using a steel column to support the corner.
At first I thought I may have to apply fire-proofing to the column per table 601, but IBC 705.2.3.1 exception 3 states balconies of Type V construction "shall be permitted to be of Type V construction and shall not be required to have a fire-resistance rating where sprinkler protection is extended to these areas". We will have spinkler protection at balconies.