retire09,
Those conex containers typically only have one door or set of doors. Section 1015.3 in
the `06 IBC requires a minimum of 2 doors to equally spaced apart. ...for egress
purposes, when the area is over 500 sq. ft., and the fuel fired equipment is over
400,000 BTU's.
Ch. 10 in the `06 IMC has some more specific requirements regarding the installation
of boilers, ...not just the 1 hr. fire rating of the enclosed area [ EX: connection to
an approved floor drain, working clearances, maintenance, etc. ].
Does your proposed conex container have or exceeed the 500 sq. ft.?
I would say that "yes, a single layer of 5/8 inch gyp. board installed on the inside
of the container would provide the 1 hr. rating". Naturally it would have to be
installed on everything including the doors, or have them "beefed up" with additional
materials to obtain the 1 hr. rating.
* *