• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Step at door (path of egress)

error404

Bronze Member
Joined
Jun 10, 2013
Messages
49
Location
United States
Let's say we needed to raise the finish floor for an entire existing Condominium unit 6". Is it allow to have a step at the door at the path of egress? See sketch below.

Project falls under the Florida Building Code (based on IBC) and the NFPA 101 Life safety

Thanks


Screenshot%202020-10-13%20170729.png
 
Looking at NFPA 101 (will exception 7.2.1.3.6 work in my favor) :

7.2.1.3.1 The elevation of the floor surfaces on both sides of a
door opening shall not vary by more than 1⁄2 in. (13 mm),
unless otherwise permitted by 7.2.1.3.5 or 7.2.1.3.6.

7.2.1.3.6 In existing buildings, a door assembly at the top of a stair shall be permitted to open directly at a stair, provided that the door leaf does not swing over the stair and that the door opening serves an area with an occupant load of fewer than 50 persons.

How about if the step is directly at the Stairways 1 / 2?

Thanks
 