Hello forum,
I am an Architect and would like to request a little feedback on this scenario:
Trying to correctly determine the number of stories for application of TABLE 504.4 ALLOWABLE NUMBER OF STORIES ABOVE GRADE PLANE
I am currently designing the building as TYPE VA & 4 stories but would much rather call it 3 stories and VB.
Currently no issues exist with the AHJ and frankly they are going to look to me to make the case.
Using 2020 NYSBC = 2018 IBC (looks to be the same language for definition)
[BG] STORY ABOVE GRADE PLANE. Any story having its finished floor surface entirely above grade plane, or in which the finished surface of the floor next above is:
Floor 3 & Floor 2 -R2 Apartments
Floor 1 - R-2, S-2 parking, small amount of M.
Basement - utility/ storage and 10% of area will have a fitness room for apartment tenant use only.
The property is flat on two sides and clearly presents as 3 stories there. The other two sides are sloping including a main road. (-10' in 166')
The calculated average grade plane around the building is 6' or less meeting item #1.
The grade around 13% of the building perimeter (80' of 645') is more than 12' (12' to 16'). potentially(?) making it 4 stories if #2 is strictly applied.
A code commentary for this section (found on this forum and attached) seems to imply wiggle room on the item #2:
"Although the criteria for establishing the first story above grade plane in Item 2 indicates that such a condition occurs where the 12-foot (3658-mm) limitation is exceeded, the application of this provision is not that simple. It is not the intent of the code to classify a story that is completely below grade except for a small entrance ramp or loading dock as a story above grade plane, provided there is no adverse effect on fire department access and staging. An analysis of the impact of such limited elevation differences is necessary to more appropriately apply the code’s intended result"
If needed I can add retaining walls and build up the grade but would rather not for other reasons.
I realize it looks like an AHJ interpretation but they are a little weak in these gray areas and I am trying to get as much backup info as possible.
If it were to be strictly applied as a 4 story building would the VA (allowable by table 504.4) be required throughout or is there away to just apply it to the part of the building over the item #2 12'. (fire walls would not really be practical but possible)
The VA construction type while appearing easy looks like a potential minefield of details depending on who is looking at it. (Based on this forum)
No extensive information on this type seems available...
Thank you In advance.
Eric
I am an Architect and would like to request a little feedback on this scenario:
Trying to correctly determine the number of stories for application of TABLE 504.4 ALLOWABLE NUMBER OF STORIES ABOVE GRADE PLANE
I am currently designing the building as TYPE VA & 4 stories but would much rather call it 3 stories and VB.
Currently no issues exist with the AHJ and frankly they are going to look to me to make the case.
Using 2020 NYSBC = 2018 IBC (looks to be the same language for definition)
[BG] STORY ABOVE GRADE PLANE. Any story having its finished floor surface entirely above grade plane, or in which the finished surface of the floor next above is:
- More than 6 feet (1829 mm) above grade plane; or
- More than 12 feet (3658 mm) above the finished ground level at any point.
Floor 3 & Floor 2 -R2 Apartments
Floor 1 - R-2, S-2 parking, small amount of M.
Basement - utility/ storage and 10% of area will have a fitness room for apartment tenant use only.
The property is flat on two sides and clearly presents as 3 stories there. The other two sides are sloping including a main road. (-10' in 166')
The calculated average grade plane around the building is 6' or less meeting item #1.
The grade around 13% of the building perimeter (80' of 645') is more than 12' (12' to 16'). potentially(?) making it 4 stories if #2 is strictly applied.
A code commentary for this section (found on this forum and attached) seems to imply wiggle room on the item #2:
"Although the criteria for establishing the first story above grade plane in Item 2 indicates that such a condition occurs where the 12-foot (3658-mm) limitation is exceeded, the application of this provision is not that simple. It is not the intent of the code to classify a story that is completely below grade except for a small entrance ramp or loading dock as a story above grade plane, provided there is no adverse effect on fire department access and staging. An analysis of the impact of such limited elevation differences is necessary to more appropriately apply the code’s intended result"
If needed I can add retaining walls and build up the grade but would rather not for other reasons.
I realize it looks like an AHJ interpretation but they are a little weak in these gray areas and I am trying to get as much backup info as possible.
If it were to be strictly applied as a 4 story building would the VA (allowable by table 504.4) be required throughout or is there away to just apply it to the part of the building over the item #2 12'. (fire walls would not really be practical but possible)
The VA construction type while appearing easy looks like a potential minefield of details depending on who is looking at it. (Based on this forum)
No extensive information on this type seems available...
Thank you In advance.
Eric