Using IBC 2006:
I have a plan for a 100' x 200' assembly building with an additional 41' of ancillary spaces (class, office, kitchen, restrooms) along the long side and on two levels. Total main level area inside the walls: 27,804 SF.
Sprinkler system is required due to capacity (>300), and area (>12,000 SF).
90% of the perimeter has over 30' clear access; the remaining 10% is at least 29'6", so I compute at least 98% for F when calculating F/P, and F/P-.25 = 73%. The perimeter increase is 73% x 6,000 = 4,380 SF.
The client wants to use wood framing, with as little fire rating as possible. Type 5B allows 6,000 SF, the sprinkler increase adds 18,000 SF (506.3) if a one story building. So the total is 6,000 + 18,000 + 4,380 = 28,380 SF and the building qualifies, if one story.
The upper level totals 8,154 inside the walls, thus is less than 1/3 of the area below (29%) and qualifies as a mezzanine. A mezzanine does not have to be open to the "room" that it is part of (505.4, Ex. 5 [not Group H or I, not more than 2 story, and is sprinklered]) and does not need to be open space ("or portions of" is used in several exceptions).
My confusion is with a portion of 505.2 that says "the enclosed portion of a room shall not be included in a determination of the floor area of the room in which the mezzanine is located". If there are no fire separations, are the ancillary spaces on the main level "enclosed"? If they are enclosed, and not part of the main level, then am I incorrect to include in the 27,804 SF when calculating the 1/3 maximum area?
My main level open and clear space in the big room is only 19,502 SF. If that is the factor to use, then the upper level way too large for a mezzanine and I have to call it a second floor, I only get a 200% increase for the sprinkler system, and construction type has to bump up to IIIB to qualify.
Is the upper level a mezzanine here?
I have a plan for a 100' x 200' assembly building with an additional 41' of ancillary spaces (class, office, kitchen, restrooms) along the long side and on two levels. Total main level area inside the walls: 27,804 SF.
Sprinkler system is required due to capacity (>300), and area (>12,000 SF).
90% of the perimeter has over 30' clear access; the remaining 10% is at least 29'6", so I compute at least 98% for F when calculating F/P, and F/P-.25 = 73%. The perimeter increase is 73% x 6,000 = 4,380 SF.
The client wants to use wood framing, with as little fire rating as possible. Type 5B allows 6,000 SF, the sprinkler increase adds 18,000 SF (506.3) if a one story building. So the total is 6,000 + 18,000 + 4,380 = 28,380 SF and the building qualifies, if one story.
The upper level totals 8,154 inside the walls, thus is less than 1/3 of the area below (29%) and qualifies as a mezzanine. A mezzanine does not have to be open to the "room" that it is part of (505.4, Ex. 5 [not Group H or I, not more than 2 story, and is sprinklered]) and does not need to be open space ("or portions of" is used in several exceptions).
My confusion is with a portion of 505.2 that says "the enclosed portion of a room shall not be included in a determination of the floor area of the room in which the mezzanine is located". If there are no fire separations, are the ancillary spaces on the main level "enclosed"? If they are enclosed, and not part of the main level, then am I incorrect to include in the 27,804 SF when calculating the 1/3 maximum area?
My main level open and clear space in the big room is only 19,502 SF. If that is the factor to use, then the upper level way too large for a mezzanine and I have to call it a second floor, I only get a 200% increase for the sprinkler system, and construction type has to bump up to IIIB to qualify.
Is the upper level a mezzanine here?