Within the same building. Fed by RMC.Do the steel conduits comply as a equipment grounding conductor all the way to the end of the circuits and the source?
Is this a subpanel for a separate building that needs a grounding electrode conductor to a grounding electrode system?
Does it matter if it is inside or outside of the same structure?If it's "within" the same building, why is it mounted outdoors? It appears to be mounted on a clapboard exterior wall.
I don't remember. This was in 2016. I think they are either 1AWG AL or 1/0ALWhat size is the neutral conductor on the supply to the panel?
Cheers, Wayne
I don't remember. This was 2016.Is this residential? Can we see the panel label? Panel schedule? Is this panel listed as "Service only"? Isolated neutral? How are the individual circuits provided an equipment ground? How far into the building does the bundling condition exist?
And you call me a Dick? Well let me help you out some. Your name is Jeff. You live in Florida. You've had concussions.I don't remember. This was 2016.
I count 12 ungrounded conductors and 11 grounded conductors. So presumably that's 10 2-wire circuits and 1 3-wire MWBC. That would make 22 CCCs, so if the conduit is long enough, the adjustment factor would be 45% per NEC Table 310.15(C)(1).It looks like there are at least 12 circuits (24 conductors) bunched together in one conduit. NEC Table B.2(11) limits ampacity to 70% of the value in Table B.2(1).
Presumably the only MWBC is the 15A double pole breaker, so the common disconnect requirement would be complied with. A little hard to tell from the picture if the blue and red from that breaker are in fact grouped with a white conductor.Shared neutrals? Do the breakers need handle ties?
The raceway entering the hub at the top of the box is RMC? I would expect that to just be threaded directly into the hub. The picture looks more like EMT going into a raintight connector going into the hub, although my familiarity with those fittings is limited.Within the same building. Fed by RMC.
If there are half the grounded conductors that there are ungrounded....How can they not be MWBC or am I just missing on that definition?Presumably the only MWBC is the 15A double pole breaker, so the common disconnect requirement would be complied with. A little hard to tell from the picture if the blue and red from that breaker are in fact grouped with a white conductor.
There are not half, you can count them in the photo. There's 11 grounded conductors (white) and 12 ungrounded (all other colors).If there are half the grounded conductors that there are ungrounded....How can they not be MWBC or am I just missing on that definition?
So I just can't count?...Whew....I thought my code was off....LOL...I don't know what I was counting...#Monday...There are not half, you can count them in the photo. There's 11 grounded conductors (white) and 12 ungrounded (all other colors).
Cheers, Wayne
Oh I'm thinking that the junction box is in the attic which places it far enough away from this enclosure to bring a bundling code into play.So most likely the conduit is just a short run to get inside the building to a box where the circuits separate out into multiple conduits.
I believe Jeff said it was raceway all the way and then that solid jumper? But maybe he was being vague to stimulate the discussion..I should probably keep my mouth shut after "Neutralgate" but whatevs....What about the equipment ground for the circuits?
All the circuits exit via a metallic conduit with a grounding bushing on it. That metallic conduit is the single EGC for all the circuits. [At least until the circuits separate, then the EGC would similarly split up.]This is supposed to be a subpanel. I see a bunch of neutrals connected to the neutral bus bar, but I don;t see any of the branch circuits with a grounding conductor to the grounding bus bar.
And the jumper correct? > the ground bar > enclosure> and maybe through the hub to the conduit > back to the source....That metallic conduit is the single EGC for all the circuits.
If that is what the picture shows, there is some controversy about the use of a (straight threaded) connector going into a (taper threaded) hub and whether that is a violation of the NEC. I haven't made up my mind about that controversy.
That tapered hub with straight threads forced into it is two things. 1. Not water tight. 2. A code violation that negates it as a EGC.Likewise, on the supply side of the panelboard, we have metallic conduit coming into a hub on the top of the enclosure. That metallic conduit is the EGC for the supply.
Pipe right to the outlet box?....Illinois wiring.....Under what circumstances would the circuit grounds mate up with the metallic conduit?
I certainly agree that if you use a straight-threaded raintight connector into female tapered threads, and the connector jams before the sealing gasket is properly compressed, it won't be water tight.That tapered hub with straight threads forced into it is two things. 1. Not water tight. 2. A code violation that negates it as a EGC.