IMO, ...Table 602 [ `09 IBC ] allows it to be rated from the interior side only,
if the exterior wall has a separation distance of more than 10 ft.
From the `09 IBC, Section 705.5 - Fire-resistance rating: "Exterior walls
shall be fire-resistance rated in accordance with Tables 601 and 602 and
this section.........The required fire-resistance rating of exterior walls with
a fire separation distance of greater than 10 feet (3048 mm) shall be rated
for exposure to fire from the inside............The required fire-resistance
rating of exterior walls with a fire separation distance of less than or equal
to 10 feet (3048 mm) shall be rated for exposure to fire from both sides."
Section 712.4 - Continuity: "Assemblies shall be continuous
without openings, penetrations or joints except as permitted by
this section and Sections 708.2, 713.4, 714 and 1022.1......Skylights
and other penetrations through a fire-resistance-rated roof deck or
slab are permitted to be unprotected, provided that the structural
integrity of the fire-resistance-rated roof assembly is maintained.
Unprotected skylights shall not be permitted in roof assemblies
required to be fire-resistance rated in accordance with Section
705.8.6..........The supporting construction shall be protected to
afford the required fire-resistance rating of the horizontal assembly
supported."
Exception: In buildings of Type IIB, IIIB or VB construction, the
construction supporting the horizontal assembly is not required to be
fire-resistance-rated at the following:
1. Horizontal assemblies at the separations of incidental uses as
specified by Table 508.2.5, provided the required fire-resistance
rating does not exceed 1 hour.
2. Horizontal assemblies at the separations of dwelling units and
sleeping units as required by Section 420.3.
3. Horizontal assemblies at smoke barriers constructed in accordance
with Section 710
Again, ...IMO, ...I believe that Table 602 provides guidance on a
specific [ rather than a general ] type of fire protection........."The
supporting type construction shall be protected" mentioned in
Section 712.4, ...is specifically allowed to be on the interior side
only, if there is a separation distance of more than 10 ft.
+ ~ ~ ~ +