R2
3 story
Type VA
Since 903.2.8 requires NFPA 13R sprinkler system, the TABLE 601 substitution for 1-hour is allowed with a Section 903.3.1.1 NFPA 13 sprinkler system because that system is not otherwise required. - Do you agree with this interpretation?
TABLE 601
note d. An approved automatic sprinkler system in accordance with Section 903.3.1.1 shall be allowed to be substituted for 1-hour fire-resistance-rated construction, provided such system is not otherwise required by other provisions of the code or used for an allowable area increase in accordance with Section 506.3 or an allowable height increase in accordance with Section 504.2. The 1-hour substitution for the fire resistance of exterior walls shall not be permitted.
903.2.8 Group R.
An automatic sprinkler system installed in accordance with Section 903.3 shall be provided throughout all buildings with a Group R fire area
903.3.1.2 NFPA 13R sprinkler systems. Automatic sprinkler systems in Group R occupancies up to and including four stories in height shall be permitted to be installed throughout in accordance with NFPA 13R.
3 story
Type VA
Since 903.2.8 requires NFPA 13R sprinkler system, the TABLE 601 substitution for 1-hour is allowed with a Section 903.3.1.1 NFPA 13 sprinkler system because that system is not otherwise required. - Do you agree with this interpretation?
TABLE 601
note d. An approved automatic sprinkler system in accordance with Section 903.3.1.1 shall be allowed to be substituted for 1-hour fire-resistance-rated construction, provided such system is not otherwise required by other provisions of the code or used for an allowable area increase in accordance with Section 506.3 or an allowable height increase in accordance with Section 504.2. The 1-hour substitution for the fire resistance of exterior walls shall not be permitted.
903.2.8 Group R.
An automatic sprinkler system installed in accordance with Section 903.3 shall be provided throughout all buildings with a Group R fire area
903.3.1.2 NFPA 13R sprinkler systems. Automatic sprinkler systems in Group R occupancies up to and including four stories in height shall be permitted to be installed throughout in accordance with NFPA 13R.