I couldn't find another thread on this subject, so I thought I'd start one.
Neither the IBC nor its Commentary address the application of Table 602 to a mixed occupancy building. I'd like to know what your thoughts are and how you apply or interpret this table for such an application.
Assume IIB construction and 4-foot fire separation distance. Building includes Groups M and A-3.
Do you:
1. Use a 2-hour exterior wall because the building contains a Group M?
2. See which occupancy the exterior wall is adjacent to and use either a 1-hour or 2-hour exterior wall as applicable?
3. Other interpretations?
Now, let's assume the building is two stories with the Group A-3 on the 2nd story which overhangs the Group M on the 1st story. The wall of the 2nd story has a fire separation distance of 4 feet and the wall of the 1st story has a 10-foot fire separation distance (i.e. 2nd story overhangs the 1st story by 6 feet).
Do you:
1. Use a 2-hour exterior wall at the 1st and 2nd stories because the building contains a Group M?
2. Use a 1-hour exterior wall at the 2nd story for the Group A-3 and no rating at the 1st story for the Group M?
3. Other interpretations?
Thanks!
Neither the IBC nor its Commentary address the application of Table 602 to a mixed occupancy building. I'd like to know what your thoughts are and how you apply or interpret this table for such an application.
Assume IIB construction and 4-foot fire separation distance. Building includes Groups M and A-3.
Do you:
1. Use a 2-hour exterior wall because the building contains a Group M?
2. See which occupancy the exterior wall is adjacent to and use either a 1-hour or 2-hour exterior wall as applicable?
3. Other interpretations?
Now, let's assume the building is two stories with the Group A-3 on the 2nd story which overhangs the Group M on the 1st story. The wall of the 2nd story has a fire separation distance of 4 feet and the wall of the 1st story has a 10-foot fire separation distance (i.e. 2nd story overhangs the 1st story by 6 feet).
Do you:
1. Use a 2-hour exterior wall at the 1st and 2nd stories because the building contains a Group M?
2. Use a 1-hour exterior wall at the 2nd story for the Group A-3 and no rating at the 1st story for the Group M?
3. Other interpretations?
Thanks!