2012 (& 2015) 2110.1.1 Exception 1.
Glass-block assemblies having a fire protection rating of not less than 3/4 hour shall be permitted as opening protectives in accordance with Section 716 in fire barriers, fire partitions and smoke barriers that have a required fire-resistance rating of 1 hour or less and do not enclose exit stairways, exit ramps or exit passageways.
Is it correct that 3/4 hour glass block is not permitted where Table 705.8 prohibits openings as applicable in exterior walls required to be of not more than 1-hour fire-resistant rated?
Glass-block assemblies having a fire protection rating of not less than 3/4 hour shall be permitted as opening protectives in accordance with Section 716 in fire barriers, fire partitions and smoke barriers that have a required fire-resistance rating of 1 hour or less and do not enclose exit stairways, exit ramps or exit passageways.
Is it correct that 3/4 hour glass block is not permitted where Table 705.8 prohibits openings as applicable in exterior walls required to be of not more than 1-hour fire-resistant rated?