Temporary Power Pole
Dennis said:
I could tell you that it probably does nothing but you probably wouldn't believe it. I am not advocating not enforcing 2 rods under normal conditions but I just don't see the need for a temp. pole Most areas here will make you drive 2 rods for the structure but only 1 for the temp. pole. For a carnival I would want more than rods if I were designing it because, IMO they are generally not capable of protecting much.
I am not aware of an exception that does not require a 2nd rod for temporary services if you cannot prove 25ohms or less resistance.
For as much as contractor complain about the interpretation of some inspectors, they don't seem to have a problem not doing things that are required because the code official "lets it go".
I bring this up because I am not a fan of the ground rod method, especially with the soils we have up this way. I do however, as an inspector try to enforce the codebook and I approve things whether or not I agree with it or like it.
Dennis said:
Absolutely-- the code in most cases will require 2 rods as one rod will not get anywhere near 25 ohms in this area-- nor will 2. I was responding in jest about being tough guys, because many areas do not enforce 2 rods for a pole. I do realize the code makes no exception for a temp. pole. On a home I use a ufer simply because the rods cannot come anywhere close to what a ufer can do-- at least around here. I got 89 ohms on 2 rods- worthless- but I got 13 ohms on a ufer on the same site. NC has amended the ufer rule and I wish they would enforce it. The rods, IMO just satisfy code and do not much more-- this is why they don't push it for a temp. pole.
We have problems with the CEE when rebar is used in footers if the electrical inspector is not involved or called during the footer inspection. Clearly a better method of grounding.
So a building inspector can't sign off on a uffer? Seems odd that an electrical inspector would be called for nothing more than a uffer. That makes me feel like I am being abused.