wwhitney
REGISTERED
If that source panel is inside the main house, then the ADU occupant needs access inside the main house. As stated in post #10.Yes and?
Adding a disconnect at the source panel (main house) and at the Subpanel (ADU) gives full "Overcurrent protection."
My understanding is that NEC 240.24(B) is not about having a single accessible OCPD for the supply protecting the occupancy, it is about having access to all the OCPD that could trip and kill power to the occupancy. To avoid the scenario where the occupant loses power due to an OCPD trip and finds they can't access the OCPD to reset it.
Of course, if that is the reasoning behind NEC 240.24(B), then there should be some exception for having properly coordinated OCPDs, where the trip curves are carefully checked and set so that the downstream OCPD always trips first.
Cheers, Wayne