SECTION 1004
OCCUPANT LOAD​
1004.1 Design occupant load.​
In determining means of egress requirements, the number of occupants for whom means of egress facilities are provided shall be determined in accordance with this section.
1004.2 Cumulative occupant loads.​
Where the path of egress travel includes intervening rooms, areas or spaces, cumulative occupant loads shall be determined in accordance with this section.
1004.2.1 Intervening spaces or accessory areas.​
Where occupants egress from one or more rooms, areas or spaces through others, the design occupant load shall be the combined occupant load of interconnected accessory or intervening spaces. Design of egress path capacity shall be based on the cumulative portion of occupant loads of all rooms, areas or spaces to that point along the path of egress travel.
apps
1004.2.2 Adjacent levels for mezzanines.​
That portion of the occupant load of a mezzanine with required egress through a room, area or space on an adjacent level shall be added to the occupant load of that room, area or space.
apps
1004.2.3 Adjacent stories.​
Other than for the egress components designed for convergence in accordance with Section 1005.6, the occupant load from separate stories shall not be added.
apps
1004.3 Multiple function occupant load.​
Where an area under consideration contains multiple functions having different occupant load factors, the design occupant load for such area shall be based on the floor area of each function calculated independently.
apps
1004.4 Multiple occupancies.​
Where a building contains two or more occupancies, the means of egress requirements shall apply to each portion of the building based on the occupancy of that space. Where two or more occupancies utilize portions of the same means of egress system, those egress components shall meet the more stringent requirements of all occupancies that are served.
1004.5 Areas without fixed seating.​
The number of occupants shall be computed at the rate of one occupant per unit of area as prescribed in Table 1004.5. For areas without fixed seating, the occupant load shall be not less than that number determined by dividing the floor area under consideration by the occupant load factor assigned to the function of the space as set forth in Table 1004.5. Where an intended function is not listed in Table 1004.5, the building official shall establish a function based on a listed function that most nearly resembles the intended function.
Exception: Where approved by the building official, the actual number of occupants for whom each occupied space, floor or building is designed, although less than those determined by calculation, shall be permitted to be used in the determination of the design occupant load.