There was a period in Southern California where a bunch of people bought EVs all at the same time (due to tax credits). They were mostly Teslas and Chevy Volts. Electric rates were still structured to drop at 8pm.
Everyone set their cars to start charging at 8pm. The problem was that all these cars had their software set linked wifi and or satellite. Even if the house meter could handle, the utility companies were getting these huge and instantaneous demand spikes. They had to work out MOUs with the manufacturers to have them update their software to randomize the start times to a range a few minutes apart, just so the utilities could ramp up without crashing the grid.
I think there must be some confusion about this Illinois law. The Act mandates that all new parking spaces in these buildings must be capable of supporting electric vehicle (EV) charging, meaning each stall needs the necessary electrical infrastructure, like a 40 amp or greater line, installed during construction. While this ensures readiness for future EV charging needs, there are valid concerns about the potential overnight demand if a significant number of EVs start using the infrastructure simultaneously, possibly totaling over 600 kWh for 40 vehicles. The Act primarily focuses on preparing infrastructure rather than immediate installation of charging stations for every space. Regarding the classification of parking garages as an Electric Energy Storage System (EESS), it's important to note that such classifications typically apply to stationary energy storage systems, not vehicles. Therefore, parking garages accommodating EVs are not classified as EESS due to the energy storage being within vehicles, which are subject to different safety standards and regulations. As EV adoption grows, developers and property managers will need to plan for scalable solutions to meet increasing demand for EV charging in residential settings.The EV car thing is quite odd to me. In Illinois there is a new law passed that now requires all parking stalls at new construction multifamily parking garages to have the capability to charge. So, ok let say there are 100 stalls, ques what? I need to make sure all stalls are capable meaning run a single 40 amp or greater line. Now, lets say we end up with 40 cars that are EV's. Overnite, 40 cars are charging basically an "electric energy storage system" of about 65-100 kWh. Total capacity would be well over 600 kWh. If this were actually considered an EESS, the parking garage would be an H-2, right? But since they are vehicles, it is not. So..., when will they make the change for an H-2 parking garage?
And a 4000A service is required...The EV car thing is quite odd to me. In Illinois there is a new law passed that now requires all parking stalls at new construction multifamily parking garages to have the capability to charge. So, ok let say there are 100 stalls, ques what? I need to make sure all stalls are capable meaning run a single 40 amp or greater line. Now, lets say we end up with 40 cars that are EV's. Overnite, 40 cars are charging basically an "electric energy storage system" of about 65-100 kWh. Total capacity would be well over 600 kWh. If this were actually considered an EESS, the parking garage would be an H-2, right? But since they are vehicles, it is not. So..., when will they make the change for an H-2 parking garage?
The premise stated 100 parking spaces so the load should be 100 EV. So that is unlikely but we are not allowed to anticipate. Another thing to consider is the 60 amp chargers. Many chargers will operate at 40 or 60 amp. The toggle between the two is part of an app. That opens the door to a 60 amp charger operating on a 50 amp circuit. It has been several years since I inspected an EV circuit. I always required a circuit that would match the maximum amperage of the charger. Nearly all were 60 amp chargers with a minimum 75 amp circuit.40 vehicles
California has a planned ban on combustion engines for everything from weed eaters to busses. The overnight electricity demand will be so great that the ground will shake. The average Mcmansion will be 600 amp and a 100 unit complex will be two 4000 amp services.And a 4000A service is required
No.And a 4000A service is required...
They just did a giant Amazon DC here with 16,000A just for the EV parking....California has a planned ban on combustion engines for everything from weed eaters to busses. The overnight electricity demand will be so great that the ground will shake. The average Mcmansion will be 600 amp and a 100 unit complex will be two 4000 amp services.
See NEC 625.42, reproduced in part below.I always required a circuit that would match the maximum amperage of the charger.
Who doesn't have a screwdriver. That's how I would check the dip switch.(1) A cover or door that requires the use of a tool to open
I was told that on occasion. I was also told that if the power went out or the wifi failed the charger had to be commissioned. In the two years since I retired the process may have tightened but the customer had the ability to reset the values.(3) Password protected commissioning software accessible only to qualified personnel"
Yet. Check in again in a few years.As to your in-depth analysis of our future EV conditions, you do make sense. There is a real chance that the entire issue becomes moot.... people are not embracing EVs in numbers sufficient to drive wholesale acceptance.
The EV car thing is quite odd to me. In Illinois there is a new law passed that now requires all parking stalls at new construction multifamily parking garages to have the capability to charge. So, ok let say there are 100 stalls, ques what? I need to make sure all stalls are capable meaning run a single 40 amp or greater line. Now, lets say we end up with 40 cars that are EV's. Overnite, 40 cars are charging basically an "electric energy storage system" of about 65-100 kWh. Total capacity would be well over 600 kWh. If this were actually considered an EESS, the parking garage would be an H-2, right? But since they are vehicles, it is not. So..., when will they make the change for an H-2 parking garage?
Required by whom or what?40 amps at 240-volts is what's required for a level 2 EV charging station.
Required by whom or what?
Cheers, Wayne
OK, sure, but then level 2 is 240V at 15A-80A.EV charging stations are classified (by whom I don't know) as level 1, level 2, and level 3.
Most of the laws already passed and the 2024IECCRequired by whom or what?
Cheers, Wayne
Illinois public act 103-005340 amps at 240-volts is what's required for a level 2 EV charging station. Does this Illinois law require level 2 charging stations, or can they be level 1? A level 1 charging station is a fairly standard 120-volt outlet and draws about 12 amps, so it can be a single 15-amp dedicated circuit.
"EV-capable" means parking spaces that have the electrical |
panel capacity and conduit installed during construction to |
support future implementation of electric vehicle charging |
with 208-volt or 240-volt or greater, 40-ampere or greater |
circuits. Each EV-capable space shall feature a continuous |
raceway or cable assembly installed between an enclosure or |
outlet located within 3 feet of the EV-capable space and a |
suitable panelboard or other onsite electrical distribution |
equipment. The electrical distribution equipment to which the |
raceway or cable assembly connects shall have sufficient |
dedicated space and spare electrical capacity for a 2-pole |
circuit breaker or set of fuses. Reserved capacity shall be no |
less than 40A 208/240V for each EV-capable space unless |
EV-capable spaces will be controlled by an energy management |
system providing load management in accordance with NFPA 70, |
shall have a minimum capacity of 4.1 kilovolt-ampere per |
space, or have a minimum capacity of 2.7 kilovolt-ampere per |
space when all of the parking spaces are designed to be |
EV-capable spaces, EV-ready spaces, or EVSE-installed spaces. |
Yes indeed, wicked fast. The problem is that most people don't know how to handle that kind of acceleration and speed, and most electric cars are not designed from the ground up with the suspension and handling that is appropriately matched for those speeds.He likes his. Wicked fast.