jar546
CBO
What do they both have in common? Very often back-fed circuit breakers. In the PV, the inverter feeds a house panel via a back-fed breaker, and with sub-panels, sometimes people just don't like using the lugs of an MLO. There are other installations that can create this situation.
NEC 408.36(D)
(D) Back-Fed Devices.
Plug-in-type overcurrent protection devices or plug-in-type main lug assemblies that are back-fed and used to terminate field-installed ungrounded supply conductors shall be secured in place by an additional fastener that requires other than a pull to release the device from the mounting means on the panelboard.
This is why I prefer commercial work and bolt-in breakers.
Based on the brand, this can be fixed for under $3

NEC 408.36(D)
(D) Back-Fed Devices.
Plug-in-type overcurrent protection devices or plug-in-type main lug assemblies that are back-fed and used to terminate field-installed ungrounded supply conductors shall be secured in place by an additional fastener that requires other than a pull to release the device from the mounting means on the panelboard.
This is why I prefer commercial work and bolt-in breakers.
Based on the brand, this can be fixed for under $3

Last edited: