Scenario: R2 3-story walk-up apartment building where each exterior exit stairway supports 4 dwelling units per floor.
The exterior exit stairway is separated from the dwelling units by 1hr fire barriers and 1hr exit access doorways. The exit access travel distance ends at the unit doors with the exit access portion of the means of egress.
Per 2021 IBC table 1006.4.3, the exit access travel distance and not the CPET is limited to 125', for buildings permitted to have a single exit. In effect there is no CPET as indicated in the commentary of 2015 and 2018. The language has changed from previous code cycles where the equivalent tables shows CPET as limited to 125'.
Is it correct that CPET doe not apply to this building?
The exterior exit stairway is separated from the dwelling units by 1hr fire barriers and 1hr exit access doorways. The exit access travel distance ends at the unit doors with the exit access portion of the means of egress.
Per 2021 IBC table 1006.4.3, the exit access travel distance and not the CPET is limited to 125', for buildings permitted to have a single exit. In effect there is no CPET as indicated in the commentary of 2015 and 2018. The language has changed from previous code cycles where the equivalent tables shows CPET as limited to 125'.