For this application 1A, but I would like dialogue from all climates.Climate?
So then once water vapor that migrates through the open cell foam hits the cold roof deck and condenses, the idea is that the foam prevents the liquid water from re-evaporating as readily as it would in the uninsulated condition?I would not use open cell for a "hot roof" design in a heating or primarily heating climate because warm moist interior air would penetrate it and condense.
Correct...condenses and rots the deck.....I just don't see how it is really any different with closed cell with the vapor from the outside....So then once water vapor that migrates through the open cell foam hits the cold roof deck and condenses, the idea is that the foam prevents the liquid water from re-evaporating as readily as it would in the uninsulated condition?
Cheers, Wayne
I believe it would result in mold and rot. I may be wrong but don't think of open cell foam as drying out real well, that it will hold the water and ice longer than fiberous insulation.So then once water vapor that migrates through the open cell foam hits the cold roof deck and condenses, the idea is that the foam prevents the liquid water from re-evaporating as readily as it would in the uninsulated condition?
Cheers, Wayne
I assume the material cost savings would be exceeded by the extra time and labor.So one method I have seen is open-cell up against the roof sheathing and then after that dries, closed-cell to finish the required thickness.
Interesting, exactly the opposite as I've seen here. I assume that in your climate people are primarily cooling spaces? Here we are primarily (exclusively) heating.So one method I have seen is open-cell up against the roof sheathing and then after that dries, closed-cell to finish the required thickness.
82F is a cool day here.Interesting, exactly the opposite as I've seen here. I assume that in your climate people are primarily cooling spaces? Here we are primarily (exclusively) heating.
We hit 82 this year, that was a record high. Like, ever.
2021 IRC R806.5(4) says "In Climate Zones 5, 6, 7 and 8, any air-impermeable insulation shall be a Class II vapor retarder, or shall have a Class II vapor retarder coating or covering in direct contact with the underside of the insulation." If I understand correctly, open cell foam would not be a Class II vapor retarder on its own, and so would require such a coating in those climate zones.Both closed cell and open cell foams are considered air impermeable. The difference is their vapor permeability.
I've seen open cell sprayed against the deck and then close cell sprayed over the top of that after it set.Open cell foam is Class IV, (very vapor open) while most closed-cell is Class II.
No venting is required by current code? Shouldn't conditioned air be supplied in that area for moisture control?The photo looks like open-cell foam sprayed with intumescent paint. This is done a lot in our CZ-4 for complex roof and ceiling shapes or on 1-1/2 storied homes. The code reference is Table R806.5.
Both closed cell and open cell foams are considered air impermeable. The difference is their vapor permeability. As long as the foam is applied directly to the roof deck and the minimum R-value in the chart above is followed, there will be no condensation and no venting is necessary. BTW, most foams today do not require the intumescent paint in an enclosed attic as they have fire retardant built-in. Most roofs are simple enough that it is more cost effective to apply insulation to the roof deck and vent the attic.
Where do you think mushrooms come from, silly?No venting is required by current code? Shouldn't conditioned air be supplied in that area for moisture control?
I think they were saying that the roof venting is not required, not that "new" space does not need conditioned. Logically, if you relocate the building envelope from the ceiling to the roof, the conditioned space increases.No venting is required by current code? Shouldn't conditioned air be supplied in that area for moisture control?