I have been working with a three story R2 apartment complex trying to control gas and charcoal grills on thier balconies and now the tenants want tiki torches.
Section 308 addresses open flames, is this where I hang my hat or is there another section to address this problem? Please give me code sections if you could.
pc
308.4 Group R occupancies.
Open flame, fire and burning in Group R occupancies shall comply with the requirements of Sections 308.1 through 308.1.6.2 and 308.4.1
308.1.6.2 Portable fueled open-flame devices.
308.1.6.2 is the one I would use. Exceptions 3 and 4 will send you to restrictions in an "A" occupancy but those requirements are also specific to the R-2
Where do you draw the line for a HOME OWNER between a tiki torch, a citronella candle, a fondue pot or birthday candles. common sense is not always so common. On another board there is a thread about a code official trying to make a sprinkler contractor sprinkler inside a revolving door. A lack of common sense there.
Education is the key here. The ones used at my nieces wedding had a canister with a wick much like an oil lamp. You could turn them upside down and they did not leak. Then again her dad is the fire prevention chief for a resort community in S Fl so I would not have expected any that was not code compliant.
308.3.1 Open-flame decorative devices.
Open-flame decorative devices shall comply with all of the following restrictions:
1. Class I and Class II liquids and LP-gas shall not be used.
2. Liquid- or solid-fueled lighting devices containing more than 8 ounces (237 ml) of fuel must self-extinguish and not leak fuel at a rate of more than 0.25 teaspoon per minute (1.26 ml per minute) if tipped over.