The picture answers the original question.Is there a secondary neutral? GECs and bonding jumpers should not be routed through lay-in lugs on bushings
EGC bonded to neutral in secondary disconnect. Notice anything odd about the GEC?
Why not? Seems perfectly normal to me. If a GEC is contained in a metal conduit, it needs to be bonded to the metal conduit at both ends, and running it through a grounding bushing would be one way to do that. And EGCs and bonding jumpers get connected to metal conduit all the time, with a grounding bushing being one way to do it.GECs and EGCs should not be routed through lay-in lugs on bushings.
The resulting sharp bends. If enough current hits the bend, it will blow out.Why not?