ETThompson
SAWHORSE
Hi
We're working on a multi-family apartment project which has an open air /covered breezeway. The owner would like to have a trash/refuse chute but no enclosed room.
We are under the Ohio Building Code 2017 which is based on the 2015 IBC. In section 713.13.3 it says these chutes have to be located "in rooms or compartments" (emphasis mine) with a 1-hour fire barrier, but I can't find any thing defining what a compartment would have to be, nor does the commentary seem to address this. Can this language support the idea of a chute just behind some sort of access door from the open-air breezeway?
Thanks, Eric
We're working on a multi-family apartment project which has an open air /covered breezeway. The owner would like to have a trash/refuse chute but no enclosed room.
We are under the Ohio Building Code 2017 which is based on the 2015 IBC. In section 713.13.3 it says these chutes have to be located "in rooms or compartments" (emphasis mine) with a 1-hour fire barrier, but I can't find any thing defining what a compartment would have to be, nor does the commentary seem to address this. Can this language support the idea of a chute just behind some sort of access door from the open-air breezeway?
Thanks, Eric