Mr. Inspector
SAWHORSE
Doing a plan review for a 8,320 sq ft steel building that the use is truck repairs. They are calling it F2. But I think it should be S2. If S2 it will need fire sprinklers but not if is F2. They did not say if there were any hazardous materials. What do you think?
2018 IBC
306.1 Factory Industrial Group F. Factory Industrial Group
F occupancy includes, among others, the use of a building or
structure, or a portion thereof, for assembling, disassembling,
fabricating, finishing, manufacturing, packaging, repair or
processing operations that are not classified as a Group H
hazardous or Group S storage occupancy.
306.2 Moderate-hazard factory industrial, Group F-1.
Factory industrial uses that are not classified as Factory
Industrial F-2 Low Hazard shall be classified as F-1 Moderate
Hazard and shall include, but not be limited to, the following:
Automobiles and other motor vehicles
311.1 Storage Group S. Storage Group S occupancy
includes, among others, the use of a building or structure, or a
portion thereof, for storage that is not classified as a hazardous
occupancy.
311.2 Moderate-hazard storage, Group S-1. Storage Group
S-1 occupancies are buildings occupied for storage uses that
are not classified as Group S-2, including, but not limited to,
storage of the following:
Motor vehicle repair garages complying with the
maximum allowable quantities of hazardous materials
listed in Table 307.1(1) (see Section 406.8)
If it did have the maximum allowable quantities of hazardous materials listed in Table 307.1(1) would it be a H?
2018 IBC
306.1 Factory Industrial Group F. Factory Industrial Group
F occupancy includes, among others, the use of a building or
structure, or a portion thereof, for assembling, disassembling,
fabricating, finishing, manufacturing, packaging, repair or
processing operations that are not classified as a Group H
hazardous or Group S storage occupancy.
306.2 Moderate-hazard factory industrial, Group F-1.
Factory industrial uses that are not classified as Factory
Industrial F-2 Low Hazard shall be classified as F-1 Moderate
Hazard and shall include, but not be limited to, the following:
Automobiles and other motor vehicles
311.1 Storage Group S. Storage Group S occupancy
includes, among others, the use of a building or structure, or a
portion thereof, for storage that is not classified as a hazardous
occupancy.
311.2 Moderate-hazard storage, Group S-1. Storage Group
S-1 occupancies are buildings occupied for storage uses that
are not classified as Group S-2, including, but not limited to,
storage of the following:
Motor vehicle repair garages complying with the
maximum allowable quantities of hazardous materials
listed in Table 307.1(1) (see Section 406.8)
If it did have the maximum allowable quantities of hazardous materials listed in Table 307.1(1) would it be a H?