jar546
CBO
Power had been disconnected and the poco required an inspection before they will provide power back to this building. When they called we told them the grounding system and bonding for the service had to be updated along with having an electrician check the connections and markings. They applied for a permit then called for inspection. We failed them for not having any grounding system at all and for having the high leg improperly marked, AND they did not know what voltage the system was.When they called for reinspection we found this cute little 3' ground rod we pulled out of the ground and this:
View attachment 1962
View attachment 1963
View attachment 1964
View attachment 1965
View attachment 1962
View attachment 1963
View attachment 1964
View attachment 1965