Yes, you can pass through a fire wall as part of your egress path. Fire walls only create separate “buildings” for area, height, and construction type requirements:For two connected buildings, separated by a fire wall, can both required/provided exits of one be via rated interior stairways that are part of the other building?
2021 IBC 503.1 General (partial quote)
For purposes of determining area limitations, height limitations and type of construction, each portion of a building separated by one or more fire walls complying with Section 706 shall be considered a separate building.
That's an interesting prospect that the code does not address. If you were treating the fire wall as a horizontal exit, then the code clearly states that no more than one-half of the exits are permitted through a horizontal exit. If you do not consider the fire wall as a horizontal exit, then there is no limitation on the number of egress paths through a fire wall.Thank you both for the reply.
RLGA,
Both buildings are of new construction. The Fire Wall is the Green dashed line, where red and blue meet, and is intended to provide structural independence. Detailing certainly will be critical.
One concern: if Building 1 were to collapse, both stairs become inaccessible to Building 2, leaving it without any exit. Would this necessitate "jogging" the firewall so that one stair is encompassed within Building 2?
Not all fire walls comply with horizontal exit requirements, such as refuge area and standpipes.Building 2 has no exits other than the two horizontal exits. NOT allowed.
The general rule is that not more than half the number or capacity of exits can be via horizontal exits. Your plan has 100% of the egress from Building 2 via horizontal exit.
This issue (all exits on the other side of a fire wall) needs to be addressed in the code.
Agreed, but only if a fire wall is used as a horizontal exit. However, the situation posed by the OP does not allude to using the fire wall as a horizontal exit.Standpipes and refuge areas notwithstanding, if the firewall actually creates two buildings and both exits are horizontal exits -- that arrangement is specifically prohibited by Section 1026.1.
A fire wall does create two buildings, but only for the purposes stated in Section 503.1 (i.e., area limitations, height limitations, and construction types). It does not, however, create two buildings for means of egress purposes. There is currently no provision in the IBC that requires a minimum of one exit on each side of a fire wall. This is where the supposed disconnect lies.If "Building 2" and "Building 1/3" are all one building and the firewall is there for some reason other than to create two buildings, then the exits through the firewall would not have to be considered horizontal exits and the analysis would change.
This may have to be with roll-up doors with a fuseable link. Then it can remain open. We had issues with Factory Mutual and Chubb when they did annual inspections of our true firewall, as all openings, other than roll-up doors, had to be below the 36" mark. So with our 35' high firewall, if we had to run conduit to the other building we had to run through the ceiling, down the firewall on one side (plastic anchors only) then run through the firewall below the 36" mark, then back up to the ceiling in the other building and continue the run from there.If you are using both walls, how do you plan on detailing the doors to ensure they remain in place should the building on either side collapse?
I would jog the fire wall so that one stair was in building #1 and the other stair is in building #2.Thank you both for the reply.
RLGA,
I’m not seeing a need for additional concern if all the stairway enclosures are on one side of the fire wall. This is a single building, references to two “buildings” are only for the purposes of analyzing allowable area, height, and type of construction per IBC 503.1.in regards to the exit enclosures being accessed from what is a separate building
Occupants in the Type IIIA “building” can freely pass through the fire wall to get to the stairs in the Type IA “building” as if this was one big Type IA building with a normal wall where the fire wall is shown.and needing to cross a fire wall with the potential to eliminate my ability to exit