Two Buildings, Shared Egress

Harrison Staab

REGISTERED
Joined
Nov 8, 2018
Messages
32
Location
Manhattan, KS
For two connected buildings, separated by a fire wall, can both required/provided exits of one be via rated interior stairways that are part of the other building?
2025.8.7_2-BLDGS-SHARED-STAIRS.png
Please note:
For purpose of this question, Building 2 is not to be considered a separate Fire Area that could be part of Building 1.
 
For two connected buildings, separated by a fire wall, can both required/provided exits of one be via rated interior stairways that are part of the other building?
Yes, you can pass through a fire wall as part of your egress path. Fire walls only create separate “buildings” for area, height, and construction type requirements:
2021 IBC 503.1 General (partial quote)
For purposes of determining area limitations, height limitations and type of construction, each portion of a building separated by one or more fire walls complying with Section 706 shall be considered a separate building.
 
Yes, but here's the tricky part: How do you plan on creating the 3-hour fire wall in conjunction with the existing wall? Is the fire wall the red line, the blue line, or both red and blue lines?

If the fire wall is the red line, there should be no problem, since you can construct it to comply with the requirements for a fire wall. If it's the blue line, does the existing wall meet the criteria for a fire wall, such as structural independence? If you are using both walls, how do you plan on detailing the doors to ensure they remain in place should the building on either side collapse?

Assuming you address the issue above, the doors can go through a fire wall provided the aggregate width of all openings in the fire wall does not exceed 25% of the length of the fire wall at each story and each opening does not exceed 156 sq. ft. (unless buildings on both sides are sprinklered throughout).
 
Thank you both for the reply.

RLGA,

Both buildings are of new construction. The Fire Wall is the Green dashed line, where red and blue meet, and is intended to provide structural independence. Detailing certainly will be critical.

One concern: if Building 1 were to collapse, both stairs become inaccessible to Building 2, leaving it without any exit. Would this necessitate "jogging" the firewall so that one stair is encompassed within Building 2?
 
Thank you both for the reply.

RLGA,

Both buildings are of new construction. The Fire Wall is the Green dashed line, where red and blue meet, and is intended to provide structural independence. Detailing certainly will be critical.

One concern: if Building 1 were to collapse, both stairs become inaccessible to Building 2, leaving it without any exit. Would this necessitate "jogging" the firewall so that one stair is encompassed within Building 2?
That's an interesting prospect that the code does not address. If you were treating the fire wall as a horizontal exit, then the code clearly states that no more than one-half of the exits are permitted through a horizontal exit. If you do not consider the fire wall as a horizontal exit, then there is no limitation on the number of egress paths through a fire wall.

This situation is certainly a possibility, so accounting for that occurrence may be wise.

This sounds like a future code change proposal...
 
Building 2 has no exits other than the two horizontal exits. NOT allowed.

1754605179496.png

The general rule is that not more than half the number or capacity of exits can be via horizontal exits. Your plan has 100% of the egress from Building 2 via horizontal exit.
 
Building 2 has no exits other than the two horizontal exits. NOT allowed.

View attachment 16182

The general rule is that not more than half the number or capacity of exits can be via horizontal exits. Your plan has 100% of the egress from Building 2 via horizontal exit.
Not all fire walls comply with horizontal exit requirements, such as refuge area and standpipes.

This issue (all exits on the other side of a fire wall) needs to be addressed in the code.
 
Not all fire walls comply with horizontal exit requirements, such as refuge area and standpipes.

This issue (all exits on the other side of a fire wall) needs to be addressed in the code.

Standpipes and refuge areas notwithstanding, if the firewall actually creates two buildings and both exits are horizontal exits -- that arrangement is specifically prohibited by Section 1026.1.

If "Building 2" and "Building 1/3" are all one building and the firewall is there for some reason other than to create two buildings, then the exits through the firewall would not have to be considered horizontal exits and the analysis would change.
 
Standpipes and refuge areas notwithstanding, if the firewall actually creates two buildings and both exits are horizontal exits -- that arrangement is specifically prohibited by Section 1026.1.
Agreed, but only if a fire wall is used as a horizontal exit. However, the situation posed by the OP does not allude to using the fire wall as a horizontal exit.
If "Building 2" and "Building 1/3" are all one building and the firewall is there for some reason other than to create two buildings, then the exits through the firewall would not have to be considered horizontal exits and the analysis would change.
A fire wall does create two buildings, but only for the purposes stated in Section 503.1 (i.e., area limitations, height limitations, and construction types). It does not, however, create two buildings for means of egress purposes. There is currently no provision in the IBC that requires a minimum of one exit on each side of a fire wall. This is where the supposed disconnect lies.

I assume the reason for the absence of such a requirement is that it is assumed the occupants can reach an exit within the prescribed travel distances, and that the potential collapse of a building would likely occur after complete evacuation. The reason for the limit on horizontal exits is that they allow a temporary holding area and extend the total distance to an exit for those egressing through them. Thus, people stay longer in the building, whether or not both sides of the horizontal exit are structurally separated by a fire wall (a horizontal exit does not require structural independence like a fire wall).
 
If you are using both walls, how do you plan on detailing the doors to ensure they remain in place should the building on either side collapse?
This may have to be with roll-up doors with a fuseable link. Then it can remain open. We had issues with Factory Mutual and Chubb when they did annual inspections of our true firewall, as all openings, other than roll-up doors, had to be below the 36" mark. So with our 35' high firewall, if we had to run conduit to the other building we had to run through the ceiling, down the firewall on one side (plastic anchors only) then run through the firewall below the 36" mark, then back up to the ceiling in the other building and continue the run from there.

My point is that there is often a disconnect between the building codes and the insurance companies' requirements for firewalls; therefore, I would do some research with them. Yes, I know many of you will say that is not our problem, but being proactive in a positive way for a better outcome is more in line with the reason for our jobs to begin with. However, if you are the designer, do your homework with the owner's insurance company and see if Chubb or Factory Mutual will audit them.
 
Thank you both for the reply.

RLGA,

Both buildings are of new construction. The Fire Wall is the Green dashed line, where red and blue meet, and is intended to provide structural independence. Detailing certainly will be critical.

One concern: if Building 1 were to collapse, both stairs become inaccessible to Building 2, leaving it without any exit. Would this necessitate "jogging" the firewall so that one stair is encompassed within Building 2?
I would jog the fire wall so that one stair was in building #1 and the other stair is in building #2.
 