Types of construction

DLC

Member
Joined
Mar 22, 2012
Messages
8
Hey guys, could you help me with a table again?

Table 601 is pretty straight forward with the exception to the A or B classification. I cant find reference anywhere to what A or B signifies.

Can ya help me out on this one?

Thanks DLC
 
I'm speaking from the California Building Code, but would assume your codes are similar: Rather simplistically, the 'A' refers to fire-rated construction and the 'B' is a non-rated construction.

Someone please correct me if I have this wrong!
 
A and B are subsets of the main construction type.

II-A is non combustible with a fire resistive rating

II-B is non combustible without a fire resitive rating

Both I-A and I-B are rated. In the other types, MT is correct.
 
IA and IB both require fire-rated constructed, so B isn't always nonrated.

I like to say that the "A" is more fire-resistive and the "B" is less fire-resistive. Depending on which one you use depaends on the building's allowable area and height.
 
Thanks for the info guys. This turned out a bit more complicated than I thought it would. Could you guys point me in the direction to find that in the book?

I am still trying to get this clear in my head.
 
Table 601. Each column identifies the fire-resistive requirements for each construction type, A and B, if applicable.

Not considering any increases, if you have a 3-story Group B building that has a maximum floor area per story of 20,000 sq. ft., then you could classify it as either Type IIB, IIIA, or IV construction. If you use Type IIB, you are not required to have any fire-resistance-rated construction; however, it must be constructed of noncombustible materials. If you use Type IIIA, you must have 2-hour exterior bearing walls, and 1-hour construction elsewhere (except interior nonbearing walls), but you can use noncombustible materials (except that exterior walls must be noncombustible or fire-retardant-treated wood). If you use Type IV, then you must comply with the heavy timber requirements.

It's a designer's choice which route they take.
 