Table 601. Each column identifies the fire-resistive requirements for each construction type, A and B, if applicable.
Not considering any increases, if you have a 3-story Group B building that has a maximum floor area per story of 20,000 sq. ft., then you could classify it as either Type IIB, IIIA, or IV construction. If you use Type IIB, you are not required to have any fire-resistance-rated construction; however, it must be constructed of noncombustible materials. If you use Type IIIA, you must have 2-hour exterior bearing walls, and 1-hour construction elsewhere (except interior nonbearing walls), but you can use noncombustible materials (except that exterior walls must be noncombustible or fire-retardant-treated wood). If you use Type IV, then you must comply with the heavy timber requirements.
It's a designer's choice which route they take.