Typo in Table 720.1(2)

Is not 2x6 lumber actually 1 1/2" x 5 1/2" and a 2x8 actually 1 1/2" x 7 1/4"?
 
There is a change bar in the 2009 edition, which identifies the 7.75-inch thick assembly as 2-hour FRR. The 2006 also has a change bar and places the 4.5-inch thick assembly in the 1-hour FRR column. The 2003 also has change bars, and 2003 Item 15-1.15 looks similar to 2009 Item 15-1.16. Maybe there is an errata for the 2006 edition, but can't check the ICC site since it's down!
 
Yikes said:
Well, as long as it's fixed now, that's the important thing.
Well ... they almost fixed it in the 2006 errata. Here's the change:

"2” x 6” wood studs at 24” centers with double top plates, single bottom plate; interior and exterior side covered with two layers of 5/8” Type X gypsum wallboard, 4’ wide, applied horizontally with vertical joints over studs. Base layer fastened with 2-1/4” Type S drywall screws, spaced 8” on center, wallboard joints covered with paper tape and joint compound, fastened heads covered with joint compound. Cavity to be filled with 5-1/2” mineral wool insulation. (posted 7-1-06)"

What they didn't change for the 2006 edition was the minimum thickness of 4 1/2" for 1 hour rating. But, the construction description fits.

For the 2009 edition the rating was increased to 2 hours and a minimum thickness of 7 3/4". But since the construction thickness totals 8" it fits the minimum also.

:confused: I really don't understand the relationship of the minimum thickness and the actual thickness of the construction as described. Unless it has something to do with footnote e to the table which allows gypsum base and plaster substitution.
 