I'm working in a 6 story building originally designed under the 97 UBC as a Type II F.R. building type. As such, all interior partitions had a minimum of 1 HR fire rating. Fast forward to today, this particular municipality has adopted the 2006 IBC. From what I understand, and you can certainly correct me if I'm wrong, the current IBC equivalent of the Type II F.R. building type from the 97 UBC is Type I-B
Table 601 in the IBC has eliminated a fire rating requirement for all non-bearing interior partitions unless it's required by another part of the code.
Question: On the 4th floor we have a new exhaust duct penetrating one existing partition before turning up and penetrating two floors and the roof deck above. The existing partition has existing penetrations that are fire caulked which was required by the original code. Do we need to maintain that and install fire dampers at the partition penetration, or does the current code override that and allow us to disregard that? If the answer is that we can disregard, is it otherwise prudent to maintain that rated condition, or is it completely unnecessary.
Thank you.
Table 601 in the IBC has eliminated a fire rating requirement for all non-bearing interior partitions unless it's required by another part of the code.
Question: On the 4th floor we have a new exhaust duct penetrating one existing partition before turning up and penetrating two floors and the roof deck above. The existing partition has existing penetrations that are fire caulked which was required by the original code. Do we need to maintain that and install fire dampers at the partition penetration, or does the current code override that and allow us to disregard that? If the answer is that we can disregard, is it otherwise prudent to maintain that rated condition, or is it completely unnecessary.
Thank you.