• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

ugly weld job

cda

SAWHORSE
Joined
Oct 19, 2009
Messages
20,964
Location
Basement
Not a welder so,

But saw one ugly vent a hood to duct weld.

welder MIG welded the joints, and it look like the haystack candy. Point things all over the place.

I should have took a picture of it.

I told him to smooth it out

ANY comments????? worse welding job I ever saw!!!!!!!!!

506.3.2 Joints, seams and penetrations of grease ducts.

Joints, seams and penetra tions of grease ducts shall be made

with a con tinuous liquid-tight weld or braze made on the external surface of the duct sys tem.

Exceptions:

1. Penetrations shall not be required to be welded or

brazed where sealed by devices that are listed for

the application.

2. Internal weld ing or brazing shall not be prohibited

provided that the joint is formed or ground smooth

and is provided with ready access for inspection.

3. Listed and labeled factory-built commercial

kitchen grease
 
Was it a internal or external weld? If it was internal, the smoothing can be required under #2. If it was on the outside of the duct, there's nothing in the code saying it has to look pretty- workmanship is not addressed. When i see ugly looking welds I spend more time checking for holes because sometimes you can only see the light shining through from one particular angle.
 
Mig welders have two types of wire. One has flux on the inside (flux core) and is used outside where there is wind. The flux provides a good welding environment. The second type uses gas, provides a pretty weld and uses solid core wire. My guess is that they went with the second option, solid wire, but ran out of gas. I think that the weld would not be as strong as one that used gas or flux core wire but a type one hood is looking for a good sealing on the duct, strength is not a consideration. If the weld looks that bad, that welder is trying to tell everyone that cares less than your could ever imagine.
 
Probably will see lots of holes after its ground smooth; careful of painted over putty or caulk to look like a weld.

weldsample.jpg


Francis
 
Yes internal weld, that could catch grease

Will do a recheck after smoothing
 
they had already started to try to smooth it out, should have taken pictures yesterday::seocnd one is a mild rep of what was there::

View attachment 629

View attachment 628

sorry not the best of picturesView attachment 628

View attachment 629

/monthly_2012_12/IMG_0579.JPG.cf7c34beb7207d0086185ea79cc0d254.JPG

/monthly_2012_12/IMG_0580.JPG.e908bd0592059ae47c9e039eca9d70fd.JPG
 
Last edited by a moderator:
Greetings,

I would find a way to flunk that even if it passed a smoke and light tests. That's peepoor welding. Could do better myself.

Merry Christmas

BSSTG
 
Don't worry, after a couple of years of not getting the exhaust system properly cleaned, the holes will be plugged with grease. Problem solved. Except for the grease that is now on the outside of the duct, where there is no fire suppression. But again, problem solved as the evidence will burn in the fire.
 