Re: uhm.... I've never seen this.
Are you permitted to use the prescriptive requirements in Table N1102.1? If you are Zone 4, it looks like you could comply as long as the windows are 0.40. If you are Zone 5, you do not have enough insulation in the exterior walls. As a rough rule-of-thumb, if the new construction in your project meets all of the requirements in the table, you stand a good chance on ResCheck, as well. If your addition does not meet all of the requirements in the Table, you will not pass ResCheck unless you provide trade-offs with insulation or U-factor beyond what is in the Table.
The first thing that I do when checking a ResCheck is to see how far the values for insulation and window U-factor deviate from the prescriptive table. Well, not really. The first that I check is location and code edition, but after that, I look compare the insulation and the windows with the prescriptive chart.
Are you permitted to use the prescriptive requirements in Table N1102.1? If you are Zone 4, it looks like you could comply as long as the windows are 0.40. If you are Zone 5, you do not have enough insulation in the exterior walls. As a rough rule-of-thumb, if the new construction in your project meets all of the requirements in the table, you stand a good chance on ResCheck, as well. If your addition does not meet all of the requirements in the Table, you will not pass ResCheck unless you provide trade-offs with insulation or U-factor beyond what is in the Table.
The first thing that I do when checking a ResCheck is to see how far the values for insulation and window U-factor deviate from the prescriptive table. Well, not really. The first that I check is location and code edition, but after that, I look compare the insulation and the windows with the prescriptive chart.