cda said:
""""non compliant systems"""what do you mean by????
also not sure if you are looking for just wet chemical or like the PIRANHAs also??
http://www.ansul.com/en/us/DocMedia/F-9788.pdf
Manufactures had wet chemical system that are wet chemical but could not meet UL 300. In the link I sent here is an example.
All WHDR-250 & 500 (Aqua-Blue) Systems were not tested to UL-300 and are also not compliant
Kidde Fire Systems
Kidde has manufactured both Dry and Wet
Chemical Systems. Their Dry Chemical
System was not tested to UL-300 Standard
so it is not compliant. All WHDR-250 &
500 (Aqua-Blue) Systems were not tested
to UL-300 and are also not compliant. The
WHDR-450 & 900 (Aqua-Blue) systems
were tested to UL-300 Standard and are
compliant. Kidde says the WHDR-450 &
900 systems were discontinued in 1998
but that does not negate the fact that they
are UL-300 compliant. All Kidde WHDR-
260, 400 & 600 Systems (current product
offering) are compliant. The style of
Control Head does not determine UL-300
compliance.