Hi
We're exploring a potential project and discussing an approach I've never seen before, which is as follows (we are under 2017 Ohio Building Code, which follows the 2015 IBC). Not having seen this before makes me think there's a problem with it...or maybe it's just too expensive...?
We were discussing a 5 over 3 podium design, wherein the upper floors residential apartments of wood construction (Construction type to be determined, although I know it would limit our heigh and stories), and a Type IA podium below. However, we're discussing if the 3rd floor (the top floor of the podium) to be residential apartments. Since they are part of the podium, they'd be of Type IA construction. The bottom two floors of the podium would be an S-2 parking garage (open or closed is not determined).
The podium is tentatively 30' high to the top, so I understand that we'd be limited in overall height by the R-2 provisions (ie, with Constr. Type VA and full 13 sprinklers, would be 40' above podium or 70' above grade plane, Type VA could be 55' above podium, 85' above grade plane).
I have not seen residential floors below the podium level previously, but I'm not sure if there's something that's specifically preventing us from doing this...is there? The code says I can have any use (except H) and since the requirements for Type IA construction are high, I can't see that I'd really be limited in area or stories. Is there something I'm missing?
Also, would each parking level be required count as a story?
Thanks
We're exploring a potential project and discussing an approach I've never seen before, which is as follows (we are under 2017 Ohio Building Code, which follows the 2015 IBC). Not having seen this before makes me think there's a problem with it...or maybe it's just too expensive...?
We were discussing a 5 over 3 podium design, wherein the upper floors residential apartments of wood construction (Construction type to be determined, although I know it would limit our heigh and stories), and a Type IA podium below. However, we're discussing if the 3rd floor (the top floor of the podium) to be residential apartments. Since they are part of the podium, they'd be of Type IA construction. The bottom two floors of the podium would be an S-2 parking garage (open or closed is not determined).
The podium is tentatively 30' high to the top, so I understand that we'd be limited in overall height by the R-2 provisions (ie, with Constr. Type VA and full 13 sprinklers, would be 40' above podium or 70' above grade plane, Type VA could be 55' above podium, 85' above grade plane).
I have not seen residential floors below the podium level previously, but I'm not sure if there's something that's specifically preventing us from doing this...is there? The code says I can have any use (except H) and since the requirements for Type IA construction are high, I can't see that I'd really be limited in area or stories. Is there something I'm missing?
Also, would each parking level be required count as a story?