1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

undermined footing

Discussion in 'Residential Foundation Codes' started by ICE, Oct 15, 2016.

  1. ICE

    ICE Sawhorse

    Joined:
    Jun 23, 2011
    Messages:
    7,552
    Likes Received:
    645
    A new sewer trench has created an issue with the footing. The footing is about 6" thick and is shallow.
    [​IMG]

    [​IMG]

    [​IMG]

    [​IMG]
     
  2. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    5,808
    Likes Received:
    668
    P2604.4.......?
     
  3. Keystone

    Keystone Sawhorse

    Joined:
    Feb 23, 2010
    Messages:
    758
    Likes Received:
    78
    Been there, done that, engineer repair was flowable fill.
    Yes, they opted for an engineer over moving the sewer...
     
  4. fatboy

    fatboy Administrator

    Joined:
    Oct 17, 2009
    Messages:
    5,471
    Likes Received:
    407
    That's what I would require, engineers evaluation.
     
  5. ICE

    ICE Sawhorse

    Joined:
    Jun 23, 2011
    Messages:
    7,552
    Likes Received:
    645
    I gave them the option of back fill with a compaction report or slurry. I didn't see a need for an engineer.
     
  6. conarb

    conarb Sawhorse

    Joined:
    Oct 22, 2009
    Messages:
    3,292
    Likes Received:
    234
    Tiger:

    Is that one of those post-tensioned slabs with a thickened perimeter? If so you definitely need an engineer who knows about post-tensioned slabs. You can tell by looking at the edges of the slab, there should be about 2" concrete plugs about 12" o.c. where they tightened the cables.
     
  7. ICE

    ICE Sawhorse

    Joined:
    Jun 23, 2011
    Messages:
    7,552
    Likes Received:
    645
    It isn't. When did post-tensioned hit the market? When I was a kid I worked around pre-stressed beams.
     
  8. conarb

    conarb Sawhorse

    Joined:
    Oct 22, 2009
    Messages:
    3,292
    Likes Received:
    234
    Tiger:

    Sometime in the 60s, it works well above grade but when they tried putting it on the ground to eliminate footings and "float", they "floated" all over the place with whole buildings going out of level, doors sticking, windows not working, etc.
     
  9. Keystone

    Keystone Sawhorse

    Joined:
    Feb 23, 2010
    Messages:
    758
    Likes Received:
    78
    I've seen post tension once, an ice rink.

    I believe several years ago someone attempted to have post tensioning in the codes. My understanding of post tensioning, used in locals with expansive soils, etc...
     