The 2023 National Electrical Code (NEC) Section 445.19 mandates provisions for the emergency shutdown of generator prime movers. This section applies to residential and non-residential installations and is intended to improve safety during maintenance and emergencies, particularly for personnel and first responders.
445.19(A) – General Requirements
Generators must be equipped with shutdown controls that meet two critical requirements:
Key Clarification: If the device serves only as an emergency shutdown (and not as the disconnecting means), it does not need to be lockable. But when it doubles as both, locking is mandatory.
Importantly, generators operating in parallel cannot use the emergency shutdown as a disconnecting means because it does not isolate the generator’s output terminals, violating 445.18(B).
445.19(B) – Remote Shutdown for Non-Dwelling Installations Over 15 kW
For all generators over 15 kilowatts in commercial, industrial, or multifamily settings, a remote emergency shutdown switch is required. This switch must:
445.19(C) – Residential Emergency Shutdowns
For one- and two-family dwellings, stationary generators (excluding cord-and plug types) must also have an emergency shutdown device installed outside the home. Like the others, it must:
While the NEC does not require grouping shutdown devices, doing so is best practice for clarity and emergency response. Authorities having jurisdiction (AHJs) should be consulted to determine the most effective and compliant installation location.
TBCF Summary
NEC 445.19 enforces clear, consistent safety measures for disabling generator prime movers in both commercial and residential applications. It distinguishes between emergency shutdown and disconnecting means, mandates mechanical reset for reliability, and prioritizes accessibility for emergency personnel. The section is critical to protecting lives during power system emergencies and ensuring proper generator maintenance procedures are followed safely.
445.19(A) – General Requirements
Generators must be equipped with shutdown controls that meet two critical requirements:
- Disable the Prime Mover Start Circuit – The shutdown mechanism must fully disable all control circuits that could initiate the prime mover. This ensures the generator cannot restart while maintenance or emergency intervention is occurring.
- Mechanical Reset Required – After shutdown, the system must require a mechanical action to reset, preventing automatic restarts without intentional human intervention.
Key Clarification: If the device serves only as an emergency shutdown (and not as the disconnecting means), it does not need to be lockable. But when it doubles as both, locking is mandatory.
Importantly, generators operating in parallel cannot use the emergency shutdown as a disconnecting means because it does not isolate the generator’s output terminals, violating 445.18(B).
445.19(B) – Remote Shutdown for Non-Dwelling Installations Over 15 kW
For all generators over 15 kilowatts in commercial, industrial, or multifamily settings, a remote emergency shutdown switch is required. This switch must:
- Be located outside the generator room or enclosure in a readily accessible location.
- Meet the same two shutdown requirements listed in 445.19(A).
- Be clearly labeled as Generator Emergency Shutdown in compliance with NEC 110.21(B).
445.19(C) – Residential Emergency Shutdowns
For one- and two-family dwellings, stationary generators (excluding cord-and plug types) must also have an emergency shutdown device installed outside the home. Like the others, it must:
- Be readily accessible.
- Disable all prime mover start circuits.
- Require a mechanical reset.
- Be properly labeled as Generator Emergency Shutdown per NEC 110.21(B).
While the NEC does not require grouping shutdown devices, doing so is best practice for clarity and emergency response. Authorities having jurisdiction (AHJs) should be consulted to determine the most effective and compliant installation location.
TBCF Summary
NEC 445.19 enforces clear, consistent safety measures for disabling generator prime movers in both commercial and residential applications. It distinguishes between emergency shutdown and disconnecting means, mandates mechanical reset for reliability, and prioritizes accessibility for emergency personnel. The section is critical to protecting lives during power system emergencies and ensuring proper generator maintenance procedures are followed safely.