Has the allowance for unenclosed stairways in the 2006 IBC been removed from the 2009?

1020.1 exceptions 8 and 9 allowed unenclosed stairways and these exceptions are not included in the 2009 code.

This is a substantial change to the design requirements of buildings.

You can no longer design buildings with attractive open stairways??

Am I missing something?
 
1020.1 Vertical Exit Enclosures changed to 1022.1 Enclosures Required.

"Change Summary: Consistent with the provisions for shaft enclosures, the fire-resistance rating of an exit enclosure cannot be less than the rating of the floor construction penetrated by the enclosure."

"The previous Exception 4 addressing the enclosure of stairways that are not a require means of egress element has been deleted. Vertical openings created by such stairways continue to be regulated under the shaft enclosure provisions of Section 708. In addition, previous Exceptions 8 and 9 have been relocated to Section 1016.1 as two exceptions in regard to the allowances for not requiring enclosure of the stairways did not change"
 
Last edited by a moderator:
Good. If an unenclosed stair is not part of the means of egress it should not be in the means of egress chapter.
 