Then I agree that there is no way it can be approved without acceptance of alternate, and 3rd party analysis required. I can only hope that doors will be added.
FM William Burns said:Texasbo,
>300 for a sprinkled facility and since they most likely will not sprinkle we have to use the >400 for non-sprinkled. Their mist delivery will not come close to a consideration for sprinkled facility however will be existent. The preliminary design has no exit doors on exterior and they will not meet the 60 or 40’ perimeter for single story in [507].
Classified as U [312.1] Greenhouses
Frank,
The roof assembly is steel and glass panel windows and noticed the smoke removal in 09.
JD,
Proposed OL is 100 employees Phase 1 and 200 with Phase 2. The total travel distance from a 12’ interior main aisle/exit access length wise is 896’ with no exit doors proposed and to the exterior walls on both sides is 471’ with no exit doors proposed.
Gene,
Correct on the process and good to know and may drop the name of your firm if OK with you?
Meeting with their DP and Engineering in the morning.