• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Unsupported Wall?

A wall is typically supported at the bottom by a slab and at the top by construction of a floor system.

The 2006 commentary:

"Lateral support at the top and bottom of the foundation

wall must be provided to resist the lateral loads imposed

on the foundation wall.

The prescriptive bottom support is provided by a

basement floor.

The top support is provided by connections and anchor

bolts as prescribed in Tables R404.1 (1) and (2)."
 
When to use Tables R404.1.2(2) through R404.1.2(7) or Table R404.1.2(8) is based on where the vertical rebar is placed; section R404.1.2.3.7.2 reads identical to the commentary for section R404.1.2.2;

“Tables R404.1.2(2) through R404.1.2(7) require the vertical steel to be located at the centerline of the wall. Table R404.1.2(8) requires the steel to be located with a maximum cover of 1¼ inches from the inside face of the wall. Tables R404.1.2(2) through R404.1.2(8) are based on reinforcing bars of Grade 60. Table R404.1.2(9) provides for use of an alternate grade of steel and bar size."

“Unsupported Wall Height” is simply the distance between the lateral support at the bottom and top of the wall. Table R404.1.2(8) footnote “e” mentions unsupported height whereas the other tables footnote “d” is a given from the table referenced.

May an expert add; confirm or deny my presumption.
 
Don't have my book but there is a section for max. unbalanced fill that is used for limiting the amount of fill you can place BEFORE the wall is laterally braced.(floor slab and floor joists.)
 